Alert not correctly detecting my trigger
Alert configuration
Query Inspector
Testing rule
  "firing": true,
  "state": "pending",
  "conditionEvals": "true = true",
  "timeMs": "162.778ms",
  "matches": [
      "metric": "Count",
      "value": 0
Thanks.
Hi alejogomezomil, what do you expect that alert return you? I mean your goal in this case is to get the last number of your query below from 1?
Thanks for answer quickly.
I expect the alert to return a green status (because the service is currently active) and not a Pending State.
I understand, you expect a OK status, that means that your condition won’t be fulfill, am I right?
It is right.
The condition isnt fullfil and the expected state should be OK.
Edit:
It is as if the condition “BELOW of 1” includes the 1 (is not an exclusive rule), so the trigger is TRUE and shows a PENDING status that is not the expected.
Maybe you should use Count() instead last().
Sory for the delay.
I tried with count() instead last(), but the result is the inverse.
The status is OK, when the service is down really.
Summary: OK always appears
with this configuration
What I tried to do is.
If query return “1” (service up), show an OK status.
If query return “0” (servide down), show an ALERTING status.
This is the data collection that I receive.
The behavior expected is an ALERTING status.
But, if I use count () instead of last (), the behavior I get is a OK status as I show in the answer above.
I see, I don’t know which is the best function for what you are trying to do. Hovewer I’ll try to look for something about your issue.
I solved it.
I setted the trigger in
when last() ABOVE 0
and also I changed the lucene query to bring me only when the monitor.status is down.
So then the alert works when detect one or more down times. (in the solution that I tried before, the alert worked when the monitor.status was less than 1)
Here is the solution: https://medium.com/sysadminas/gerando-alertas-de-uma-monitora%C3%A7%C3%A3o-do-heartbeat-atrav%C3%A9s-do-grafana-parte-2-26552f5709fd